Replies: 2 comments 6 replies
-
This is intended. BT improves the internal algorithm of your Thermostat by setting its target heatping point to a extreme value. You can (and should) install the BT Card (https://github.com/KartoffelToby/better-thermostat-ui-card) this UI component displays the actual heating target. |
Beta Was this translation helpful? Give feedback.
4 replies
-
I have the same issue. When heating up from Eco (18°) in the morning to 21,5° the target temperature jumps unintended to 28°. I'm using the BT card. I have to set back the target temperature manually to 21,5° several times until it stays there. |
Beta Was this translation helpful? Give feedback.
2 replies
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment
-
I have some TRV combined with an external sensor in BT. When I set a target temperature - 19° for example - manually
some moments later BT changes the target temp without any sense
Can’t see anything in the log, as no action is listed. How can I solve this? Calibration via offset is not available in the config and mode ‘AI time based’ shows the same behaviour.
The debug log after setting target to 20° for example:
2024-03-04 10:06:51.608 DEBUG (MainThread) [custom_components.better_thermostat.climate] better_thermostat Heizungen Wohnbereich: HA set target temperature to 20.0 & None 2024-03-04 10:06:51.614 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Heizungen Wohnbereich: TO TRV set_temperature: climate.heizung_esszimmer from: 35.0 to: 21.5 2024-03-04 10:06:51.619 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Heizungen Wohnbereich: climate.heizung_esszimmer / check_target_temp / _last: 21.5 - _current: 35.0 2024-03-04 10:06:54.621 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Heizungen Wohnbereich: TO TRV set_temperature: climate.heizung_spielzimmer from: 35.0 to: 21.5 2024-03-04 10:06:54.625 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Heizungen Wohnbereich: climate.heizung_spielzimmer / check_target_temp / _last: 21.5 - _current: 35.0 2024-03-04 10:06:57.628 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Heizungen Wohnbereich: TO TRV set_temperature: climate.heizung_wohnzimmer from: 35.0 to: 24.5 2024-03-04 10:06:57.632 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Heizungen Wohnbereich: climate.heizung_wohnzimmer / check_target_temp / _last: 24.5 - _current: 35.0 2024-03-04 10:06:57.774 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Erdgeschoss Heizungen: TRV climate.heizung_esszimmer update received 2024-03-04 10:06:57.774 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Erdgeschoss Heizungen: trigger_trv_change / _old_heating_setpoint: 35.0 - _new_heating_setpoint: 21.5 - _last_temperature: 35.0 2024-03-04 10:06:57.774 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Erdgeschoss Heizungen: TRV climate.heizung_esszimmer decoded TRV target temp changed from 35.0 to 21.5 2024-03-04 10:06:57.775 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Erdgeschoss Heizungen: TRV climate.heizung_esszimmer update received 2024-03-04 10:06:57.775 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Erdgeschoss Heizungen: trigger_trv_change / _old_heating_setpoint: 35.0 - _new_heating_setpoint: 21.5 - _last_temperature: 22.0 2024-03-04 10:06:57.775 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Erdgeschoss Heizungen: TRV climate.heizung_esszimmer decoded TRV target temp changed from 35.0 to 21.5 2024-03-04 10:06:57.776 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Heizungen Wohnbereich: TRV climate.heizung_esszimmer update received 2024-03-04 10:06:57.777 DEBUG (MainThread) [custom_components.better_thermostat.utils.helpers] better_thermostat Erdgeschoss Heizungen: climate.heizung_esszimmer / heating_power_valve_position - temp diff: 0.7 - heating power: 0.0113 - expected valve position: 62% 2024-03-04 10:06:57.777 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Erdgeschoss Heizungen: TO TRV set_temperature: climate.heizung_esszimmer from: 35.0 to: 30.5 2024-03-04 10:06:57.778 DEBUG (MainThread) [custom_components.better_thermostat.utils.helpers] better_thermostat Erdgeschoss Heizungen: climate.heizung_esszimmer / heating_power_valve_position - temp diff: 0.7 - heating power: 0.01 - expected valve position: 70% 2024-03-04 10:06:57.778 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Erdgeschoss Heizungen: TO TRV set_temperature: climate.heizung_esszimmer from: 22.0 to: 31.5 2024-03-04 10:06:57.783 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Erdgeschoss Heizungen: climate.heizung_esszimmer / check_target_temp / _last: 30.5 - _current: 21.5 2024-03-04 10:06:57.786 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Erdgeschoss Heizungen: climate.heizung_esszimmer / check_target_temp / _last: 31.5 - _current: 21.5 2024-03-04 10:06:58.060 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Erdgeschoss Heizungen: TRV climate.heizung_spielzimmer update received 2024-03-04 10:06:58.060 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Erdgeschoss Heizungen: TRV climate.heizung_spielzimmer update received 2024-03-04 10:07:00.634 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Heizungen Wohnbereich: TO TRV set_temperature: climate.heizung_flur from: 19.5 to: 20.5 2024-03-04 10:07:00.639 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Heizungen Wohnbereich: climate.heizung_flur / check_target_temp / _last: 20.5 - _current: 35.0 2024-03-04 10:07:00.785 DEBUG (MainThread) [custom_components.better_thermostat.utils.helpers] better_thermostat Erdgeschoss Heizungen: climate.heizung_flur / heating_power_valve_position - temp diff: 0.7 - heating power: 0.0113 - expected valve position: 62% 2024-03-04 10:07:00.786 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Erdgeschoss Heizungen: TO TRV set_temperature: climate.heizung_flur from: 21.0 to: 29.5 2024-03-04 10:07:00.787 DEBUG (MainThread) [custom_components.better_thermostat.utils.helpers] better_thermostat Erdgeschoss Heizungen: climate.heizung_flur / heating_power_valve_position - temp diff: 0.7 - heating power: 0.01 - expected valve position: 70% 2024-03-04 10:07:00.787 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Erdgeschoss Heizungen: TO TRV set_temperature: climate.heizung_flur from: 35.0 to: 31.5 2024-03-04 10:07:00.792 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Erdgeschoss Heizungen: climate.heizung_flur / check_target_temp / _last: 29.5 - _current: 35.0 2024-03-04 10:07:00.792 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Erdgeschoss Heizungen: climate.heizung_flur / check_target_temp / _last: 31.5 - _current: 35.0 2024-03-04 10:07:02.433 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Erdgeschoss Heizungen: TRV climate.heizung_wohnzimmer update received 2024-03-04 10:07:02.433 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Erdgeschoss Heizungen: TRV climate.heizung_wohnzimmer update received 2024-03-04 10:07:02.740 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Erdgeschoss Heizungen: TRV climate.heizung_flur update received 2024-03-04 10:07:02.742 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Heizungen Wohnbereich: TRV climate.heizung_flur update received 2024-03-04 10:07:03.284 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Erdgeschoss Heizungen: TRV climate.heizung_flur update received 2024-03-04 10:07:03.286 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Heizungen Wohnbereich: TRV climate.heizung_flur update received 2024-03-04 10:07:03.793 DEBUG (MainThread) [custom_components.better_thermostat.utils.helpers] better_thermostat Erdgeschoss Heizungen: climate.heizung_spielzimmer / heating_power_valve_position - temp diff: 0.7 - heating power: 0.0113 - expected valve position: 62% 2024-03-04 10:07:03.793 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Erdgeschoss Heizungen: TO TRV set_temperature: climate.heizung_spielzimmer from: 22.0 to: 30.5 2024-03-04 10:07:03.794 DEBUG (MainThread) [custom_components.better_thermostat.utils.helpers] better_thermostat Erdgeschoss Heizungen: climate.heizung_spielzimmer / heating_power_valve_position - temp diff: 0.7 - heating power: 0.01 - expected valve position: 70% 2024-03-04 10:07:03.794 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Erdgeschoss Heizungen: TO TRV set_temperature: climate.heizung_spielzimmer from: 35.0 to: 31.5 2024-03-04 10:07:03.800 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Erdgeschoss Heizungen: climate.heizung_spielzimmer / check_target_temp / _last: 30.5 - _current: 21.5 2024-03-04 10:07:03.802 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Erdgeschoss Heizungen: climate.heizung_spielzimmer / check_target_temp / _last: 31.5 - _current: 21.5 2024-03-04 10:07:03.927 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Erdgeschoss Heizungen: TRV climate.heizung_flur update received 2024-03-04 10:07:03.929 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Heizungen Wohnbereich: TRV climate.heizung_flur update received 2024-03-04 10:07:03.929 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Heizungen Wohnbereich: trigger_trv_change / _old_heating_setpoint: 29.5 - _new_heating_setpoint: 31.5 - _last_temperature: 20.5 2024-03-04 10:07:06.801 DEBUG (MainThread) [custom_components.better_thermostat.utils.helpers] better_thermostat Erdgeschoss Heizungen: climate.heizung_wohnzimmer / heating_power_valve_position - temp diff: 0.7 - heating power: 0.0113 - expected valve position: 62% 2024-03-04 10:07:06.801 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Erdgeschoss Heizungen: TO TRV set_temperature: climate.heizung_wohnzimmer from: 35.0 to: 31.5 2024-03-04 10:07:06.803 DEBUG (MainThread) [custom_components.better_thermostat.utils.helpers] better_thermostat Erdgeschoss Heizungen: climate.heizung_wohnzimmer / heating_power_valve_position - temp diff: 0.7 - heating power: 0.01 - expected valve position: 70% 2024-03-04 10:07:06.803 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Erdgeschoss Heizungen: TO TRV set_temperature: climate.heizung_wohnzimmer from: 35.0 to: 32.5 2024-03-04 10:07:06.808 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Erdgeschoss Heizungen: climate.heizung_wohnzimmer / check_target_temp / _last: 31.5 - _current: 24.5 2024-03-04 10:07:06.809 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Erdgeschoss Heizungen: climate.heizung_wohnzimmer / check_target_temp / _last: 32.5 - _current: 24.5 2024-03-04 10:07:08.082 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Erdgeschoss Heizungen: TRV climate.heizung_spielzimmer update received 2024-03-04 10:07:08.084 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Heizungen Wohnbereich: TRV climate.heizung_spielzimmer update received 2024-03-04 10:07:08.084 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Heizungen Wohnbereich: trigger_trv_change / _old_heating_setpoint: 21.5 - _new_heating_setpoint: 30.5 - _last_temperature: 21.5 2024-03-04 10:07:08.084 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Heizungen Wohnbereich: TRV climate.heizung_spielzimmer decoded TRV target temp changed from 20.0 to 30.5 2024-03-04 10:07:08.090 DEBUG (MainThread) [custom_components.better_thermostat.utils.helpers] better_thermostat Heizungen Wohnbereich: climate.heizung_esszimmer / heating_power_valve_position - temp diff: 9.7 - heating power: 0.01 - expected valve position: 100% 2024-03-04 10:07:08.090 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Heizungen Wohnbereich: TO TRV set_temperature: climate.heizung_esszimmer from: 21.5 to: 35.0 2024-03-04 10:07:08.095 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Heizungen Wohnbereich: climate.heizung_esszimmer / check_target_temp / _last: 35.0 - _current: 21.5 2024-03-04 10:07:10.622 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Erdgeschoss Heizungen: TRV climate.heizung_wohnzimmer update received 2024-03-04 10:07:10.623 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Erdgeschoss Heizungen: trigger_trv_change / _old_heating_setpoint: 24.5 - _new_heating_setpoint: 31.5 - _last_temperature: 31.5 2024-03-04 10:07:10.624 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Heizungen Wohnbereich: TRV climate.heizung_wohnzimmer update received 2024-03-04 10:07:11.097 DEBUG (MainThread) [custom_components.better_thermostat.utils.helpers] better_thermostat Heizungen Wohnbereich: climate.heizung_spielzimmer / heating_power_valve_position - temp diff: 9.7 - heating power: 0.01 - expected valve position: 100% 2024-03-04 10:07:11.097 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Heizungen Wohnbereich: TO TRV set_temperature: climate.heizung_spielzimmer from: 21.5 to: 35.0 2024-03-04 10:07:11.102 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Heizungen Wohnbereich: climate.heizung_spielzimmer / check_target_temp / _last: 35.0 - _current: 30.5 2024-03-04 10:07:11.116 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Erdgeschoss Heizungen: TRV climate.heizung_wohnzimmer update received 2024-03-04 10:07:11.117 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Erdgeschoss Heizungen: trigger_trv_change / _old_heating_setpoint: 31.5 - _new_heating_setpoint: 32.5 - _last_temperature: 31.5 2024-03-04 10:07:11.118 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Heizungen Wohnbereich: TRV climate.heizung_wohnzimmer update received 2024-03-04 10:07:12.596 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Erdgeschoss Heizungen: TRV climate.heizung_spielzimmer update received 2024-03-04 10:07:12.597 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Erdgeschoss Heizungen: trigger_trv_change / _old_heating_setpoint: 30.5 - _new_heating_setpoint: 31.5 - _last_temperature: 30.5 2024-03-04 10:07:12.597 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Erdgeschoss Heizungen: TRV climate.heizung_spielzimmer decoded TRV target temp changed from 21.5 to 31.5 2024-03-04 10:07:12.597 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Erdgeschoss Heizungen: TRV climate.heizung_spielzimmer update received 2024-03-04 10:07:12.597 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Erdgeschoss Heizungen: trigger_trv_change / _old_heating_setpoint: 30.5 - _new_heating_setpoint: 31.5 - _last_temperature: 31.5 2024-03-04 10:07:12.599 DEBUG (MainThread) [custom_components.better_thermostat.utils.helpers] better_thermostat Erdgeschoss Heizungen: climate.heizung_esszimmer / heating_power_valve_position - temp diff: 10.7 - heating power: 0.0113 - expected valve position: 100% 2024-03-04 10:07:12.599 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Erdgeschoss Heizungen: TO TRV set_temperature: climate.heizung_esszimmer from: 30.5 to: 35.0 2024-03-04 10:07:13.506 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Erdgeschoss Heizungen: TRV climate.heizung_esszimmer update received 2024-03-04 10:07:13.506 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Erdgeschoss Heizungen: trigger_trv_change / _old_heating_setpoint: 21.5 - _new_heating_setpoint: 31.5 - _last_temperature: 31.5 2024-03-04 10:07:13.508 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Heizungen Wohnbereich: TRV climate.heizung_esszimmer update received 2024-03-04 10:07:14.103 DEBUG (MainThread) [custom_components.better_thermostat.utils.helpers] better_thermostat Heizungen Wohnbereich: climate.heizung_wohnzimmer / heating_power_valve_position - temp diff: 9.7 - heating power: 0.01 - expected valve position: 100% 2024-03-04 10:07:14.104 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Heizungen Wohnbereich: TO TRV set_temperature: climate.heizung_wohnzimmer from: 24.5 to: 35.0 2024-03-04 10:07:14.108 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Heizungen Wohnbereich: climate.heizung_wohnzimmer / check_target_temp / _last: 35.0 - _current: 32.5 2024-03-04 10:07:14.584 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Erdgeschoss Heizungen: TRV climate.heizung_esszimmer update received 2024-03-04 10:07:14.584 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Erdgeschoss Heizungen: trigger_trv_change / _old_heating_setpoint: 31.5 - _new_heating_setpoint: 35.0 - _last_temperature: 31.5 2024-03-04 10:07:14.586 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Heizungen Wohnbereich: TRV climate.heizung_esszimmer update received 2024-03-04 10:07:15.538 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Erdgeschoss Heizungen: TRV climate.heizung_esszimmer update received 2024-03-04 10:07:15.538 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Erdgeschoss Heizungen: trigger_trv_change / _old_heating_setpoint: 35.0 - _new_heating_setpoint: 30.5 - _last_temperature: 31.5 2024-03-04 10:07:15.540 DEBUG (MainThread) [custom_components.better_thermostat.events.trv] better_thermostat Heizungen Wohnbereich: TRV climate.heizung_esszimmer update received 2024-03-04 10:07:15.605 DEBUG (MainThread) [custom_components.better_thermostat.utils.helpers] better_thermostat Erdgeschoss Heizungen: climate.heizung_flur / heating_power_valve_position - temp diff: 10.7 - heating power: 0.0113 - expected valve position: 100% 2024-03-04 10:07:15.606 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Erdgeschoss Heizungen: TO TRV set_temperature: climate.heizung_flur from: 29.5 to: 35.0 2024-03-04 10:07:15.610 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Erdgeschoss Heizungen: climate.heizung_flur / check_target_temp / _last: 35.0 - _current: 31.5 2024-03-04 10:07:17.109 DEBUG (MainThread) [custom_components.better_thermostat.utils.helpers] better_thermostat Heizungen Wohnbereich: climate.heizung_flur / heating_power_valve_position - temp diff: 9.7 - heating power: 0.01 - expected valve position: 100% 2024-03-04 10:07:17.109 DEBUG (MainThread) [custom_components.better_thermostat.utils.controlling] better_thermostat Heizungen Wohnbereich: TO TRV set_temperature: climate.heizung_flur from: 20.5 to: 35.0
Beta Was this translation helpful? Give feedback.