Aquara E1 heating value differences #1508

Closed Answered by folfy
PrzemekEsteves asked this question in Q&A
Discussion options

You must be logged in to vote

That's how BT works - It offsets the error of your thermostats temperature sensor. If you set 24°C, your room has 21.2°, but your TRV thinks it's 19.3°, BT will set 24° + (19.3° - 21.2°) = 22° (rounded down).

If you don't want BT to apply calibration, choose the "no calibration" mode in the configuration flow of your entity / thermostat.

Replies: 1 comment

Comment options

You must be logged in to vote
0 replies
Answer selected by PrzemekEsteves